1/12/2011 2:13 AM | |
Joined: 10/7/2005 Last visit: 9/10/2025 Posts: 3049 Rating:
|
Hello --SerdaR-- I suggest youuse the "Help on Event" button of the Diagnostic Buffer popup window instead which will give you the following info for Event 3x83: Cause: The operating system has detected an accumulation of memory errors that were detected and removed by the CPU hardware. To correct or avoid errors: Check the plant installation for EMC problems. Hint: If you can't find the Event anymore in the Diganostic Buffer (e.g. its been pushed out due to other events thathave come and gone), simply do the following: 1.) Usethe "Help on Event" on any event 2.) Click on the "Index" buttonat the top of the help screen and you'll get a complete lits of all event numbers and associated help. Last but not least, you''ll find some good advise on EMC compliant installation for your PLC in the Automation System S7-400 Hardware and Installation manual. I hope this helps |
Cheers |
|
1/12/2011 9:37 AM | |
Joined: 1/11/2011 Last visit: 4/16/2025 Posts: 6 Rating:
|
thanx UMENCHO. i will change that CPU. |