The HMI uses always the time of its operating systems to timestamp the messages. So, you need to synchronize the time between your HMI and the PLC: http://support.automation.siemens.com/WW/view/en/24104104 Another possibility is to use the message alarm process (very complicated, but uses always the timestamp of the PLC, needs much less ressources on the bus, and synchronizes acknowlede of alarms between all HMI): http://support.automation.siemens.com/WW/view/en/24013249 |