4/10/2025 8:32 AM | |
Joined: 8/3/2009 Last visit: 9/5/2025 Posts: 16349 Rating:
|
Hello Carmendomar_95 Your WInCC Version is too old. You need WinCC V7.5Sp2 Upd4 or newer that you can use the Secure HMI connection from the Newer S71500/1200 FW versions. In your case you can only switch off the secure HMI Connection. Check theses FAQs: https://support.industry.siemens.com/cs/de/en/view/109798498 https://support.industry.siemens.com/cs/de/en/view/109805946 Bye Murof |
If this Information really helps, you could use the Rate function |
|
Follow us on