Dear all, I am facing one problem from couple of months that my profibus networkgoes down for some milli seconds and restore back, because of this our steel making process got affected and there is a cobble in the mill. Can anyone helps on this issues. For reference i am attaching the network topology. Following steps are already taken to resolve this issue but still the problem is not resolved:- 1. Checking of cable with Profibus analyzer, voltage looks OK in every node.2. Change the ET200 m Module in each RIO3. Changed the power supply in the cabinets4. Changed the Connectors5. Change completely all the Profibus cable and PCF cable6. Proper Grounding of Profibus with Panel7. Separate cable routing for this system no interference from Power Cables8. Reduced the Baud Rate to 187.5 Kbps9. We had separate earthing for the METCS system also. Internal et200m is connected to profibus and from panel to panel it is connected through FO cable (OBT). No FO cable length is more than 45 meters node to node. There is not any single node drop but any of the node can drop from time to time. Sometimes this problem not occurs for couple of months and sometimes it happened on weekly basis.