6/16/2022 5:42 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello Samantha1255, Please follow below steps. 1. If axis active measurement system is no 2 i.e. external encoder, you need to change it to 1 i.e. motor encoder. To do so, change axis MD 30200 = 1. Do not change any other encoder related parameter. 2. Check axis MD 32450 value, set it to 0, if not 0. 3. Please check your PLC logic, for active reference signal. Check DB3x.DBX1.5 should be active i.e. motor encoder measuring must be active. If your machine has incremental referencing system, you need to modify your PLC logic so that motor encoder referencing will become active. After checking & modifying above values, carry out referencing & check axis backlash. Hope this helps. |