4/6/2020 6:35 PM | |
Posts: 24 Rating:
|
Hello, I got the not enough memory at the time of program download (only changes)in spite of having enough free memory. I just change the properties of one bit in the PLC data type ( I checked setpoint), and then when I tried to download it says there is not enough memory. I took a screenshot which is attached. Do you think that it means total download? Thanks. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/07/2020 08:09:12New subject after splitting |
|
4/7/2020 3:26 PM | |
Joined: 7/7/2010 Last visit: 9/10/2025 Posts: 16084 Rating:
|
Are you using a memory card? If so, your memory card may be too small to hold the current version of the project and the new version that needs copying. I ran across something similar with an s7-1500 where the memory card was too small. I had to perform a factory reset before I could load changes to the plc. Better answer is to get the next size larger memory card (if that is the problem).
|
science guy |
|
11/28/2022 4:46 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
|
New question published by MaP_17 is split to a separate thread with the subject When downloading a DB with a data volume of more than 16383 bytes, TIA-Portal reports errors.. Best regards |
Follow us on