6/4/2017 9:42 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Some points regarding your questions: 1- A redundant system in main rack and I/O terminals should be designed in a manner that loss of a single module doesn't shut down the plant. 2-Failure of any module can be detected in software both in PCS 7 and STEP 7.You need to change any faulty module immediately after failure to avoid loss of toatal redundancy. 3-Mean time between failure(MTBF) of modules used in S7-400H systems can be found in THIS manual and this FAQ.More points regarding maintenance can be found on page 253 of S7-400H manual. I hope it helps, hdhosseini |
Last edited by: hdhosseini at: 6/4/2017 9:45:47 AM |
|
This contribution was helpful to
1 thankful Users |
6/4/2017 12:09 PM | |
Joined: 7/21/2010 Last visit: 2/4/2024 Posts: 54 Rating:
|
thanks alot. it is helpful. |
6/6/2017 7:44 AM | |
Joined: 12/9/2010 Last visit: 10/8/2022 Posts: 623 Rating:
|
Hi ameic, The siemens products have defined characteristics regarding power, hazardous conditions. U must select hardware by taking into consideration the hazardous atmosphere in the plant. Another serious cause of failure is due to power fluctuations. Proper precautions/measures should be implemented in the panel to avoid dangers. Redundancy and hot swap-able modules can prevent production loss. |
If you like the comment, rate it (right top) or thank it (left bottom). |
|
Follow us on