I would start by investigating PLC's diagnostics buffer, to see the cause of the faults. |
1/4/2021 3:49 PM | |
Joined: 7/7/2010 Last visit: 9/12/2025 Posts: 16094 Rating:
|
Use the online TIA Selection Tool ( TIA Selection Tool | Totally Integrated Automation (TIA) | Siemens Global ) and populate the PLC rack with your exact components. It will suggest a power module (PM) to be placed somewhere in the midst of all that IO to provide enough power for the communications BUS.
|
science guy |
|
This contribution was helpful to
1 thankful Users |
1/5/2021 12:37 AM | |
Posts: 2 Rating:
|
Yes, I was able to figure out the issue last week. I placed a system power supply in the beginning of the bus on the TIA Selection Tool and it worked. Thank you!
|