hello im tring to conect to a plc logo simens but aperas an error "unabe to access the remote device" i attachement some photos of the error im using a plc logo ref. 6ED1052-1MD08-0BA2 hardware type logo! 8 (0BA8.STANDART) Attachmentlogo.docx (117 Downloads) |
12/5/2024 5:12 PM | |
Joined: 12/18/2014 Last visit: 9/2/2025 Posts: 35912 Rating:
|
The LOGO! 6ED1052-1MD08-0BA2 is the current LOGO! 8.4, not a 0BA8.Standard. For this LOGO! 8.4 you need LSC V8.4.x if you want to communicate between LOGO! and LSC. And I think you have the firmware not updated. The image of the shows that the firmware is V1.84.02 (X|3|4). You ca download the update for LSC to LSC V8.4.1 and the firmware update to V1.84.03 from here: Firmware update for LOGO! 8.4 basic devices and service pack 1 for LOGO! Soft Comfort V8.4 |
12/5/2024 5:33 PM | |
Joined: 10/20/2022 Last visit: 12/5/2024 Posts: 28 Rating:
|
witch i have to download? Download of the entire package Upgrade for LOGO! Soft Comfort, LOGO! Web Editor and Firmware update for LOGO! 8.4 basic devices: V8.4.1_Upgrade_Package_SW_FW.zip(5.1 GB)(SHA-256) Download for LOGO! Web Editor V1.2.1: LOGO_Web_Editor.zip(1.2 GB)(SHA-256) Download for firmware update for LOGO! 8.4 basic devices: 109975994_LOGO8.4_Service_Pack1_FW.zip(13.7 MB)(SHA-256) |
12/5/2024 5:54 PM | |
Joined: 12/18/2014 Last visit: 9/2/2025 Posts: 35912 Rating:
|
|
12/5/2024 6:20 PM | |
Joined: 10/20/2022 Last visit: 12/5/2024 Posts: 28 Rating:
|
THANKS ITS RESOLVED |