12/30/2008 4:26 PM | |
Posts: 271 Rating:
|
Hello Norman, Here's a note on one possibility: http://support.automation.siemens.com/WW/view/en/24040602 Attached is a Adobe PDF that may help you in the future. Troubleshooting as you probably know is to isolate things. One way to isolate problems with Infeed Regen Modules is to remove the logic interface and use toggle switches to trigger the enables, disconnect the DC bus from other power modules and such, and disconnect the electronic equipment bus from other modules as well. Allow the unit to standalone from your entire drive system and see if it comes up properly by itself or not. Hope this helps... AttachmentIR Module Troubleshooting.pdf (2548 Downloads) |
This contribution was helpful to
1 thankful Users |
12/30/2008 6:14 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating:
|
It is a godd GuideApplication (PDF-Document) |
Karl |
|