3/4/2010 11:20 AM | |
Posts: 661 Rating:
|
1) LOGO! TD has no "clear program" option. This cannot be the reason. 2) A program is stored in the LOGO! base module "forever". Power failure doesn´t matter. LOGO! cannot loose the program without manipulation. I can imagine only following scenarios: 1) Disconnection of the programming cable or abort of the data transfer while downloading 2) An emtpy card has been inserted and LOGO! read the empty program from the card. 3) "Clear user program and password" has been used (SW feature) 4) LOGO! has been used in combination with a copy protected memory card. If then the card is pulled out, LOGO! is empty. Plug this card again, then it will work as before (after reading the card) The E-Stand (development status) is a matrix, printed on the housing. http://support.automation.siemens.com/WW/view/en/18298033 But as Helmut wrote: In your case, the E-Stand is not reason for your problem. With ES4, the TD has new feature. |
3/4/2010 12:37 PM | |
Joined: 1/17/2007 Last visit: 10/6/2020 Posts: 289 Rating:
|
Thank you Fux and Helmut for the support. |