3/28/2016 11:21 AM | |
Posts: 3 Rating:
|
Can any one tell us if my PLC is working on modbus. I want to use micromaster 420 vfd. How to operate the VFD o modbus? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 3/29/2016 10:53:49 AMNew subject after splitting |
|
3/28/2016 2:40 PM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello Rus; The MM420 drive does not have a Modbus interface. See the attached screenshot, showing all allowed communication interfaces for this drive family. It is taken from the following manual, section 3.7: Operating Instructions: MICROMASTER 420 0,12 kW - 11 kW https://support.industry.siemens.com/cs/ww/en/view/24523400 Your options are: USS (RS-232 or RS-485,, directly on the drive terminals, or Profibus-DP, CAN or DeviceNet, with a special communications module. Hope this helps, Daniel Chartier |
This contribution was helpful to
2 thankful Users |
3/29/2016 9:02 AM | |
Joined: 4/28/2015 Last visit: 4/19/2025 Posts: 10876 Rating:
|
Hello, look how simple it is: https://www.google.sk/?gfe_rd=cr&ei=7Cf6VpqvK8ak8weZp7fACg&gws_rd=ssl#q=uss+modbus+converter |
With best regards... |
|
3/29/2016 9:38 AM | |
Posts: 3 Rating:
|
Can I get this converter from simens directly so that it would be easy for me. |
4/15/2016 1:45 PM | |
Posts: 198 Rating:
|
uss Modbus protocol converter. |
4/15/2016 4:49 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Instead of MM420 You can use SINAMICS G120 with : |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |