Hello. What is the sources of speed setpoints to these drives? Did you compare setpoints in both drives?
|
11/23/2013 12:22 AM | |
Posts: 21 Rating:
|
hi KSN thanks for answer, if you can tell me the parameter number where i can see the speed setpoint please. I attached the diagnosis of the PLC
AttachmentDiagnose CPU PDV-47_ Bloc de notas.pdf (230 Downloads) |
11/23/2013 12:09 PM | |
Joined: 8/25/2006 Last visit: 9/12/2025 Posts: 2218 Rating:
|
Hello. As you post PLC diagnostic, I assume, your PLC controlling both drives. Look in the PLC program how the setpoints are formed for both drives. Then compare that setpoints inside drives. Look at themanual, chapter 8 'Function diagrams', sheet G152. Begin from parameter P625 and go back through all setpoint channel (G137, G136, G135 etc).
|