Hello nepiter you do not have listed which FW Version your PLC has and which Image Versino your Panel. It s because only newer HMI Image Versios do work with the Secure HMI communication. for example: https://support.industry.siemens.com/cs/de/en/view/109820712 also you should care about the Date/time of your Panel. The Basic Panels do not have a retentive Clock, so it will only synch if your establish a connection to the PLC... but this will not work if the panel time is out of the validity area of the certificate. So a NTP Server connection would be the best solution in this situation. Also you should not make a certificate with startdate 1970... Use realistic timeranges You do not have to transfer the certificate manually, it will be sent by project transfer from TIA Portal. you do not have to care about it Bye Murof |