12/14/2023 8:18 AM | |
Joined: 5/6/2022 Last visit: 7/10/2025 Posts: 589 Rating:
|
Hi Roby, In these cases there are a number of questions that can be very helpful to be able to see what may be going wrong: - What is the exact version and reference of the PLC and HMI? - Is it a direct connection or does it go through some intermediate element, such as a router? - Does the date and time set in PLC and HMI match? - Within the PLC properties, is any password protection against HMI access configured? If so, has this password been configured in the "HMI connection" for the panel to access? - In the PLC variables table, are the variables shared with the HMI marked "Accessible from HMI/OPC" and "Writable from HMI/OPC"? I also share with you some FAQs that you can review, in case of certificate issues as you comment for example: "No connection to PLC after WinCC Panel Images V17 Update 6". Best regards! |
If this Information really helps, you could use the Rate function |
|
10/31/2024 1:49 PM | |
Joined: 7/22/2020 Last visit: 1/5/2025 Posts: 1 Rating:
|
Hello Roby I have the same problem as you describe. Have you found the solution? Thank you |