7/5/2013 7:12 AM | |
Posts: 39 Rating:
|
Hiiii, Which power factor is more suitable leading or lagging? |
7/5/2013 7:47 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Unity power most suitable. In this case active power = reactive power (KW=KVA) |
7/5/2013 8:04 AM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating:
|
Hello, Lagging vs. leading is another way of saying the net reactance is either inductive or capacitive. This is slightly simplistic, and what we are talking about above is really DPF, or Displacement Power Factor. Non-linear loads don't really shift the current waveform, they distort it. The current waveform starts to look like a square wave, and square waves contain harmonics. So non-linear loads add harmonic distortion, and this tends to mimic a capacitively reactive load, adding some leading power factor. So when we say power factor, we really must include DPF plus harmonic distortion in total. Read entire story here |
VANDE MATARAM..... |
|
This contribution was helpful to
1 thankful Users |
7/5/2013 5:40 PM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
Hello I just want to add - in industry you will find PF always lagging or near to unity Leading pf may have some worst effect specially on generator - here is one note on that More on this - you can google it - this is very basic of electricals and you will find a lot nice explanation Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|