2/19/2017 4:44 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, 6SN1146-1AB00-0BA0 is 5/10 KW unregulated infeed module which converts AC supply into DC. 6SN1123-1AA00-0AA1 is 15 A power module which converts DC supply to AC. LT power module is feed DC supply via DC power bus & control supply via data bus. Please check 3 phase AC supply is present at power supply terminals of infeed module. Next check the control terminals 63, 64 i.e. pulse enable & drive enable are present. Also check 9,112, 48 & NS1, NS2 & AS1 As2 terminal status. Please refer the attached sheet for more information. Attachment611 Infeed module.pdf (364 Downloads) |
2/21/2017 5:35 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, IF three phase is available at power terminal U1, V1, W1 & if 1U1-2U1; 1V1-2V1; 1W1-2W1 are shorts then GREEN LED on infeed must light. It indicates control power supply is healthy. If it is not then control supply is faulty. When NS1 NS2 on X171 are short, then internal pre-charging contactor will get ON & when pulse enable & drive enable signals are present, DC output bus will be charged. Please refer the attached sheet for more information. So in your case, even if 3 phase supply is present at U, V & W & at 2U1, 2V1, 2W1 & GREEN LED is not ON, then in this case control power supply of infeed module is faulty. HTH. AttachmentInfeed module ckt dia.pdf (358 Downloads) |
This contribution was helpful to
1 thankful Users |
3/5/2017 4:28 AM | |
Joined: 10/17/2007 Last visit: 9/15/2025 Posts: 4452 Rating:
|
Hi, Friend, I see you are not new member--Sept. 2014. and Thanks PISCEAN 2010--He is very kind of member to answer your questions. If i were He, i will not or saying I CANNOT answer your questions. If you are new in this field you need follow some suggestion--did you see my suggestion at the top of this forum branch and CNC branch--if you want to get better help. you need at least post one picture of your system, which you think they have trouble. Normally SIMODRIVE 611 system cannot work alone, they are controlled by CNC or PLC, specially 611U can run by itself . you mentioned Power supply, power section(or call drive module) but you only write # in half of 611 control card 6SN1118--. what is very important for the last part of #.THEY SHOULD LIKE THIS 6SN1118-0NH01-0AA1 or some thing else Now I can only give you one suggestion--you said your system no any light (LED) on. did you hear anty of fan running or not. Basically, you need to check Power supply module 1st, 6SN1146-1AA00-0AA1 Check manual PISCEAN 2010 send to you.you separate drive , test power supply only if power is dead--of cause there will no any thing work in the whole system OK try to post pictures and answer basic question--make other understand what is system and what is your problem
|
If you like my comments please |
|
Follow us on