8/6/2023 5:59 PM | |
Joined: 8/27/2021 Last visit: 3/18/2024 Posts: 5 Rating:
|
Good day. I want read Temperature from TCW210-th data logger with Modbus TCP/IP. My Siemens logo 8 ip is 192.168.1.20 and TCW210 data logger ip is :192.168.1.40 . Logo 8 is client and TCW210 is Server in Modbus protocol (Port:502) . command is requesting the content of holding registers 19800 and use converter float to integer but cannot reading temperature data, Please help me. Best Regards Abolfazl Ghanbarzadeh
------------------------------------------------------------------------------------------ Attachmenttcw210-th-temperature-humidity-data-logger-user-manual-r1.13 (1).pdf (540 Downloads) |
Last edited by: Jen_Moderator at: 08/07/2023 10:46:43New subject after splitting |
|
8/6/2023 6:04 PM | |
Joined: 12/18/2014 Last visit: 9/4/2025 Posts: 35918 Rating:
|
Please upload your program as a ZIP file. |
8/6/2023 6:45 PM | |
Joined: 8/27/2021 Last visit: 3/18/2024 Posts: 5 Rating:
|
hello. The PLC program and the file of the table of commands and addresses of Modbus will be sent to your service attachment. Thanks a lot AttachmentModbus TCW210th.zip (382 Downloads) |
8/6/2023 7:49 PM | |
Joined: 12/18/2014 Last visit: 9/4/2025 Posts: 35918 Rating:
|
That's not what I asked for. Can you show me the register table?
|
8/6/2023 8:03 PM | |
Joined: 8/27/2021 Last visit: 3/18/2024 Posts: 5 Rating:
|
Address table is in page 40 Attachmenttcw210-th-temperature-humidity-data-logger-user-manual-r1.20.pdf (536 Downloads) |
8/6/2023 8:06 PM | |
Joined: 8/27/2021 Last visit: 3/18/2024 Posts: 5 Rating:
|
Address table |
8/6/2023 8:06 PM | |
Joined: 12/18/2014 Last visit: 9/4/2025 Posts: 35918 Rating:
|
You upload a PDF file with 9 pages. How do I see page 40? |
8/6/2023 8:19 PM | |
Joined: 12/18/2014 Last visit: 9/4/2025 Posts: 35918 Rating:
|
The LOGO! cannot create custom telegrams. You have to specify this in the Modbus connection table.
|
Follow us on