11/16/2012 6:14 AM | |
Posts: 21 Rating:
|
Good morning ladies and gentlmens We got the problem with the Simoreg 6RA7085. Our Simoreg was used as exitation system of SinchMotor. Someday the A067 had occur on PMU. After it operator stopped SinchMotor (the reason was not the A067). Unfortunattely, nobody could check r0013 for real temperature and nobody could reset A067. And after opertaor disenergized system with Simoreg. Then They decided to lauch system and enegized Simoreg. F040 had occur certanly. But it doesnt reset for now. When we came to there what we had to do: Checked r0013 - -47(low level) Р947.9 - 4 Р949.9 - 2 I could not to connect to Simoreg by DriveMonitor, but i done this few days later without problems on other Simoreg Then I puted out the cable from X6:X7(Temp Sensor), r0013 didnt change. I mesured the resistanse - 7,4kOm - its strange for temp sensors. After i simulated the PT100 signal rom calibrator on the x6:x7 terminal and r0013 didnt change. So F040 doent reset for now. Somebody advice change the CUD1 in the same case/tf/WW/en/Posts/13939 Is it correct that CUD1 must be changed or we need any other means to find the reason of this problem?
|
Last edited by: boyn84 at: 11/16/2012 6:16 AM |
|