12/9/2020 9:23 PM | |
Posts: 5 Rating:
|
Hello Guys! Good day, I just want to ask how much is the maximum number of Interface module (ET 200MP) that can be connected to S7 1500. Thanks in advance. |
12/10/2020 8:05 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hi Azimuth it depends on the type of S7-1500 CPU and the technical spec will give these details. For example, a 1516-3 PN/DP (6ES71516-3AN02-0AB0) has an overall limit of 1000 distributed I/O devices that can be connected via AS-i, PROFIBUS or PROFINET. Note that each port has its own limits too, which in the 1516-3 PN/DP case are:
To get to the 1000 device limit you'll need to add Communication modules and in this case can have up to 8 additional CM's (and check each CM's limit of number of connectable devices). Last but not least, you would also want to check the overall I/O module number and I/O address area limits in the tech spec too. |
Cheers |
|
This contribution was helpful to
3 thankful Users |
12/11/2020 11:23 PM | |
Posts: 5 Rating:
|
Fritz, Thank you very much for the quick and clear answer. Cheers! Azimuth |
This contribution was helpful to
1 thankful Users |