Set P082=1 and make optimization again P051=25, in this case optimization runs for armature and field supply. |
3/1/2016 7:23 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Is this the same job or different? If yes, is your problem solved? Now please read this manual, chapter 7.5 & follow steps for start up of drive. HTH |
9/15/2017 8:58 PM | |
Posts: 3 Rating:
|
We face the same problem with the same drive and was solved by reducing set point in p102 |
12/15/2017 12:36 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
|
New question published by Mubashir Jalil is split to a separate thread with the subject SIMOREG 6RA70 DC and RPM's. Best regards |