1/22/2010 2:53 PM | |
Posts: 2 Rating:
|
Thanks for the reply. Yes, I have looked closely at the configuration of this parameter. There exists a serial interface board in the drive which the hardwired "Run" command is maintained on PL6 terminals . The parameter P554 contains the value 2001 (SST 1, Word 1 bit 0). When the drive disconnect is cycled and the run maintained the drive remains in the (008) ON LOCKED mode and will not re-start until the "Run" is toggled. I have included the drawing I have for the drive showing the connection detail. Is this configuration workable for auto restart? Attachment20100122074220.pdf (300 Downloads) |