Please refer FD 8513 (Is attached here with for ready reference), control word 1 bit 2 is for OFF3. It is controlled via P558. This is operated by CB data word 1 bit 2 i.e. B3102. So need to check this if it is 0 it means quick stop command is applied to drive. You need to connect drive monitor to check the status of Control word 1 or can check on PMU at r550. HTH. AttachmentMasterdrive MC OFF3 .pdf (594 Downloads) |