11/17/2022 10:45 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Please check below points. 1. Have you locked motor during current controller optimisation? Please provide DCM article number & connected motor nameplate details here. Please refer SINAMICS DCM DC converters, Operating Instructions, Firmware Version V1.5 operating manual & SINAMICS DCM, List Manual, Firmware version 1.5 (based on 5.1 SP1) manual wherein you will get all parameter & fault related information. Hope this helps. |
Last edited by: Jen_Moderator at: 11/17/2022 13:57:16Links optimized. |
|
This contribution was helpful to
1 thankful Users |
11/18/2022 5:56 AM | |
Joined: 11/17/2022 Last visit: 11/18/2022 Posts: 2 Rating:
|
hi, thank for you helping me thank you ps after all, where can we see the decryption of the codes in 50047 parameter. ([0] - "108.000" [1] - 11). in the documentation you listed earlier, isn't? |
11/18/2022 6:42 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, It looks like non standard application as such the fault code displayed in your case is not available in standard list manual. Please check entered motor related parameters values & verify those are correct as per installed DC power module & motor nameplate rating/connection. BTW have you consulted Siemens before selection of CM with options for subject application? I suggest you to contact your nearest Siemens service/support center or raise support request. |