Hi Mike, Thank you for your attention and reply! As you mentioned in your reply we changed the type of the command of a Switch. We used SC (Single Command) instead of DC (Double Command) (Attached PDF Page1). Then We used Simulator to send the command through IEC-101 (Attached PDF Page2). But the command did not execute. In the IED (BCU) received command is shown as SEL-Close and SEL-Open ( Most probably it means Select open and Select close) (Attached PDF Page3). In the same BCU when we used another Double Command for another switch command was executed properly. In Our project control center use separated telegram addresses (IOA) for Open and Close. Do we need to change any setting for this in SICAM Pas or BCU? Is it possible using SoftPLC for this purpose? AttachmentPas Command.pdf (775 Downloads) |