2/13/2011 1:36 PM | |
Joined: 10/23/2007 Last visit: 2/19/2023 Posts: 5 Rating:
|
Dear all Splitted from Cannot reset F 011. |
Last edited by: O_Moderator at: 2/14/2011 10:34 AMnew subject after splitting |
|
2/15/2011 3:22 AM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
Check out following simillar to your case.. /tf/WW/en/Posts/54065 And for F011, as Grame said, use Search and you will find lots of discussion and all possibilities of this fault.. Although you are not getting F029 but also check this..
Regards, Devesh Vithani |
Last edited by: Vithani at: 2/15/2011 3:29 AMI dont Like people driving Fast, thats the reason I overtake them ;) |
|
2/15/2011 5:10 AM | |
Posts: 27 Rating:
|
Check VSB for wrong sensing of DC bus voltage.For F011, check r949 for which phase is showing overcurrent then check CT,its connections or replace CT. |
2/16/2011 3:32 PM | |
Joined: 10/23/2007 Last visit: 2/19/2023 Posts: 5 Rating:
|
Dears Vithani & Graeme With best regards Falcon7 |
11/24/2018 8:02 AM | |
Posts: 1 Rating:
|
First , check your CT . It may be the culprit mostly. |