Netpro's "main job" is for configuring communication connections, you typically do not want to "clutter" your Netpro screen with DP Slaves (it is HWconfig's "job" to configure these). If you do however want to see DP Slaves in Netpro you'll need to go to the <View> menu and select <With DP Slaves / IO Devices> (so this couldn't be the cause of your problem, I'm still glad you solved it somehow though). |
Last edited by: fritz at: 07.07.2009 01:26Cheers |
|
8/4/2011 9:29 AM | |
Posts: 69 Rating: (0) |
I deleted SDBs many time! but I don't think I did that online! I have to be online with CPU then do that? Moreover, I did the compile from Simatic Manager! |
8/4/2011 9:54 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
At least you could try it. What happens if you remove the new added module and tried to download the "old" hardware configuration? Try to put there some other module (non physically existing with you) and try to download it. http://support.automation.siemens.com/WW/view/en/8686578 Best regards, Hristo Mihalev |