10/29/2012 8:16 PM | |
Joined: 9/13/2010 Last visit: 11/6/2024 Posts: 30 Rating: (1) |
Please post the content of diagnostic buffer. |
7/31/2013 4:24 PM | |
Joined: 9/2/2012 Last visit: 8/15/2024 Posts: 711 Rating: (30) |
Haibsrchandru, in cpu property, check the startup configuration. make it as run instead of mode prior to power off. now try this-- make remote station healthy(make sure startup is complete) after that give supply to plc and see the status. regards vipz
|
|
|
4/6/2014 12:49 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Thanks vipz Your suggestion will certainly help me to bring the CPU to RUn Mode, if we switch the power off and then ON again. However what we are trying to do is to prevent the CPU from going to STOP Mode if one or More Profinet Node Fails. Will adding OB82 to the program prevent this ? Cheers Navnag |
There is no such thing as the last bug in a program |
|
4/8/2014 12:12 PM | |
Posts: 18 Rating: (0) |
Dear Chandru, I belive that have u changed startup after power on to "warm restart-Run" as attached image with this . Am i right ?? |