3/8/2012 8:56 PM | |
Joined: 6/4/2008 Last visit: 8/16/2024 Posts: 1492 Rating: (323)
|
Hi Rubin, The A017 alarm does exist in CU2 (Even though it is not in the manual - I have had this before due to a transistor fault) 1/. If your drive does not have an option code (-Z K80) then the safe off function can be ignored. An internal hardware fault can also cause a simulated safe off (to protect hardware) 2/. Change P052=3 to upload a complete set of parameters. 3/. I don't either and I work for Siemens 4/. Correct!! 5/. Yes, set P733 = 1 and supply the DC bus with 24V, WITH NO MOTOR connected, you can run the drive and use an oscilloscope to check the drive pulses. But I think the A017 will stop you here, you need to determine what is wrong or repair first.. First thing I would do is to use a diode test across all phases and the DC bus and also between the DC Bus to the motor output terminals. That is 24 separate measurements - see the attached for a clue. Regards, Graeme
AttachmentDrive_Tests.pdf (526 Downloads) |
5/12/2016 8:16 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (876) |
Please read the reply of Rubin & try by replacing IVI/IGD from Fibre optic to Flatband type. |
8/11/2016 10:03 PM | |
Posts: 94 Rating: (2) |
Dear friend Try replace the optical fiber cables |