7/28/2014 12:03 PM | |
Joined: 6/2/2010 Last visit: 4/2/2024 Posts: 41 Rating:
|
Dear sir, How to do Auto tuning PID algorithm in s7- series. Regards, Kusha |
7/28/2014 1:51 PM | |
Posts: 1058 Rating:
|
Hello kusha, PID algorithm in step7 is available in SFB41/FB41. For documentation on how to implement it look here: FAQ: Where can you find descriptions and examples of PID control with FB 41 Reference manual "System Software for S7-300/400 System and Standard Functions" Manual "S7-300 Automation System CPU 31xC Technological Functions" FAQ: Reversing the direction of control action of the controller "CONT_C" FAQ: What should you watch out for when calling and assigning parameters to the controller functions in function blocks (S)FB41, (S)FB42 and (S)FB43 Manual: Commissioning a CPU 31xC: Closed-loop control So if you have an auto tuning algorithm, this information should help you to implement it. regards |
Last edited by: eisenpferdreiter at: 7/28/2014 1:52 PM |
|
7/31/2014 1:25 PM | |
Joined: 1/28/2009 Last visit: 6/11/2024 Posts: 6841 Rating:
|
Hello, Just to add my comments over Tuning algorithms for SIMATIC S7 (specifically S7-300/400):
I also suggest reading the following most interesting PID TAGS:
Hamid Hosseini |
This contribution was helpful to
1 thankful Users |
Follow us on