1/10/2011 2:08 PM | |
Posts: 17 Rating: (0) |
Hi all I want to run drive with PLC S7-200via signal4-20mA. how itcould be possible, please guide me that which parameter do i change. |
1/10/2011 2:29 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181)
|
Hello, Basically you need functional diagram 80 (where to connect the 4-20mA signal, scaling it...) and functional diagram 316 (assignment of setpoint channel). Find them in SIMOVERT MASTERDRIVES Vector Control Compendium VC34 (Operating Instructions) (on 507th or 509th page and from 543th). Best regards, Hristo Mihalev |
Last edited by: UMENCHO at: 1/10/2011 2:31 PM |
|
1/10/2011 2:41 PM | |
Posts: 17 Rating: (0) |
Thank you dear for sharing the knowlege |