6/28/2019 11:10 AM | |
Posts: 1283 Rating: (105) |
Are you talking about scaling ? |
6/28/2019 11:21 AM | |
Posts: 8 Rating: (0) |
i scaled it like 0V = 0A, and 1V = 30A but i don't know if that will work or if i need to apply ohm law |
Last edited by: Bacelo at: 06/28/2019 11:22:00 |
|
6/28/2019 11:25 AM | |
Posts: 1283 Rating: (105) |
which PLC you are using? can you share some screenshots? |
6/28/2019 11:40 AM | |
Posts: 8 Rating: (0) |
Sure, i'm using a s7-1200 DC/DC/DC and here's a print of my function right now. |
6/28/2019 12:16 PM | |
Posts: 1283 Rating: (105) |
0-1V is very low resolution to play with i think. i had attached values for 0-10V |
Last edited by: Jay. at: 06/28/2019 12:18:07 |
|
6/28/2019 12:24 PM | |
Posts: 8 Rating: (0) |
ok but the sensor gives me values betwhen 0-1V do i need an external circuit to amplify the signal ? |
7/13/2019 4:15 PM | |
Joined: 5/6/2010 Last visit: 8/26/2024 Posts: 1977 Rating: (275) |
Hello Bacelo, you can use a signal conditioner to transducer 0..1 V to 0..10 V. e.g. Signal conditioner - MACX MCR-UI-UI-UP-NC - 2811297 from Phoenix Contact. This part can you configure with DIP-switches at the front, it's very easy. The precision of this signal conditioner is better than 0.1 %. Then you have a resolution of 30 A / 27648 = 1 mA regards |
This contribution was helpful to1 thankful Users |