Are you really trying to connect a sensor to a AM2 AQ module? That is a analog output module. For more information how to connect your sensor, read this thread: /tf/WW/en/Posts/51426#top |
Problem solved? |
|
12/15/2010 12:02 PM | |
Joined: 4/22/2010 Last visit: 2/15/2024 Posts: 5697 Rating: (713) |
The wiring diagram is in the zipfile witch you can find at the link i posted earlyer. Logo 4-20 mA AM2 loop powered.doc. Again, you cannot connect the sensor to a AM2 AQ module ! You need a AM2 inputmodule. Program examples are on the Siemens Logo site. https://www.automation.siemens.com/mcms/programmable-logic-controller/en/logic-module-logo/application-examples/Pages/Default.aspx Have a look at the Correct scaling of a 4-20mA sensor example |