Hello Lee; Are you refering to this document? - SIMATIC S7-1200 und S7-1500: Changing TO parameters https://support.industry.siemens.com/cs/af/en/view/109810890 Could you tell us what PLC you are working with, what software version are you programming it with, and what problems you are facing? Hope this helps, |
9/27/2022 9:49 AM | |
Joined: 4/28/2015 Last visit: 9/20/2024 Posts: 397 Rating: (56)
|
Hello Lee, did you have a look to the manual?
See chapter 8.2.15. (page 320) The tag structure "<TO>.Modulo.<tag name>" contains the configuration of the modulo function. See chapter 8.1.1. (page 293) RES = Restart: Changes to the start value in the load memory are made using the extended instruction "WRIT_DBL" (write to DB in load memory). Changes will not take effect until after restart of the technology object. Restart is done with MC_RESET (chapter 7.2 - page 219). Set input "Restart" = TRUE. Maybe this will help... And please tell us, wich controller you use - Thanks! |