Hello MH-Karami; This depends on whether you want to acknowledge the horn signal from on;ly the servers or from the clients. To create the horn tags in the clients, follow the procedure in this document: - How is the horn editor configured for single-user stations, servers, redundant servers and client OS stations in SIMATIC PCS 7 / WinCC? https://support.industry.siemens.com/cs/ww/en/view/17778088 -Note: Create acknowledgement tag in the clients: “This procedure is only required if you wish to perform multiple acknowledgment on the connected OS client stations using "acknowledgment tags". You require another tag in this case. Create this internal tag in the same group and ensure that you perform a "project-wide update" for these tags.” Hope this helps, Daniel Chartier |