11/24/2017 10:03 PM | |
Joined: 9/27/2006 Last visit: 9/14/2025 Posts: 12408 Rating:
|
Hello mans_electro; Based on the error message you show: Is it possible that HSC1 is already used, or that the input address selected for HSC1 is used for another purpose in your program? See Chapter 6, page 118 +, High Speed Counter instructtions, and the tab;ele of HSC addresses and modes below, from the S7-200 System manual: Hope this helps, Daniel Chartier |
Last edited by: Jen_Moderator at: 11/27/2017 6:51:43 AMInserted righ link. |
|
This contribution was helpful to
1 thankful Users |
11/25/2017 5:33 PM | |
Posts: 4 Rating:
|
thnx Daniel Chartier I created a new project that contains only of HSC1 (basic configuration) !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! |
11/26/2017 3:48 PM | |
Joined: 9/27/2006 Last visit: 9/14/2025 Posts: 12408 Rating:
|
Hello mans_electro; For some reason your CPU is not accepting the wizard settings because it sees that the HSC you are attempting to create is a modification of an existing configuration. I would suggest that you bring back the S7-200 CPU to factory settings, using WIPEOUT.exe as shown in the following FAQ, and then attempt to create a new project once again: https://support.industry.siemens.com/cs/ww/en/view/2123168 It is always recommended to make an upload of the existing settings and progrm before you use wipeout, as everything i the PLC memory will be erased. Hope this helps, |
Last edited by: Jen_Moderator at: 11/27/2017 6:52:52 AMInserted right link. |
|