6/3/2021 7:15 PM | |
Joined: 11/8/2017 Last visit: 9/6/2024 Posts: 335 Rating: (186)
|
Hi, From what I understand, the new PXC4 and PXC5 controllers are currently best suited for small projects/integrations. The range will be expanded over time, and with this should come larger capacity devices that would be better suited to your application. We faced a similar capacity issue with a PXC4.E16 recently. The controller is capable of using 40 physical I/Os, and 40 Modbus points. Trend Logs are limited to 40 - so full logging wasn't possible. BA objects are limited to 300 (262 used, just with the 80 points) - which doesn't leave much space for anything else. We simply blame the sales-person. Although the controller limits are not published on the individual controller data sheets, the limits are however published in document A6V11973797 (PXC4 & PXC5 Planning Overview). See HERE. (Page 10). Regards, |
6/4/2021 9:28 AM | |
Joined: 8/27/2016 Last visit: 7/19/2024 Posts: 29 Rating: (0) |
Hope Siemens upgrade firmware for PXC4, PXC5 to solve this limitation. David |