6/27/2011 10:13 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating:
|
Hello Ekalavya, Thanks for your reply. I have checked the parameters which you have mentioned. But those parameters are not matching with the motor nameplate parameters. That is why I am unable to understand. So few nameplate parameters I have mentioned in my thread. Why this is so? Hope now my question is clear. |
6/27/2011 10:25 AM | |
Posts: 2964 Rating:
|
Hello Deep, I agree the parameter what you have mentioned and what i have mentioned there difference. May be the OEM would have got some error during the commissioining of this motor and would have changed for working this motor.... Regards, Ekalavya |
6/27/2011 10:58 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating:
|
Or the motor was changed... Best regards, Hristo Mihalev |
6/27/2011 11:50 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating:
|
Hello Ekalavya & UMENCHO, Thanks for your reply. The machine at present is under commissioning. I have checked the motor & from the nameplate it is confirmed that the motor MLFB no is correct one. May be, as you have pointed out, the controller may be commissioned for some other motor. Let us see what happens when power is switched ON. |