5/4/2020 7:51 PM | |
Joined: 12/18/2014 Last visit: 6/17/2024 Posts: 33204 Rating: (4107)
|
Yes, in your case this is normal. You have created two connections manually, so 2 connections are already occupied. Now you have also connect to 2 Modbus devices using drag & drop. With Drag & Drop, own connections created by the software are used. Are 2 connections again, so a total of 4. The maximum number you can read in the manual, see attachment. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 pages 29+30.pdf (256 Downloads) |
5/4/2020 8:26 PM | |
Joined: 12/18/2014 Last visit: 6/17/2024 Posts: 33204 Rating: (4107)
|
The manually created connections are designed so that you can also map inputs and outputs via them. |
5/4/2020 8:44 PM | |
Joined: 12/18/2014 Last visit: 6/17/2024 Posts: 33204 Rating: (4107)
|
See attachment... |
5/4/2020 8:48 PM | |
Joined: 12/18/2014 Last visit: 6/17/2024 Posts: 33204 Rating: (4107)
|
The user Scorp once created this Excel sheet.
AttachmentModbus Implementierungstabelle.pdf (239 Downloads) |
This contribution was helpful to1 thankful Users |
5/4/2020 11:13 PM | |
Posts: 40 Rating: (0) |
Then I'm probably missing something obvious... I'm using this example to read holding registers, convert float to int, etc. In the example memory variable is used to feed F/I function block with the input data. Now I want to use the same connection to the same Modbus server for my Network Input and Output. For now I can easily use the same connection to read DI and write Coil [from the Logo], but for reading the HR (like in example) I always get a separate connection. Please advise. |
Last edited by: Jen_Moderator at: 05/05/2020 09:02:05Optimized link. |
|