Hello zamani, |
4/8/2011 8:13 PM | |
Joined: 9/27/2006 Last visit: 5/21/2024 Posts: 12257 Rating: (2668) |
Hello zamani; You have 2 questions here, and they are not completely related. So: First, migration from version 5 to version 7 of WinCC is exoplained in this FAQ: How do you migrate WinCC projects to new versions of WinCC from V4 to V7? You cannot go directly to version 7, as the database server has changed in version 6, and features of version 5 are not supported in the same way in version 7. So study the procedure and determine how you will proceed. Second, Modbus serial drivers were provided by Allmendinger in v. 5, but were no longer supported by version 6.2, as discussed in the following thread. The basic recommendation is that you use the OPC channel to access your Modbus data in version 7, it will also allow you to connect to Excel for data acquisition. /tf/WW/en/Posts/9441 and How can you write values from WinCC to a Microsoft Excel table? Hope this helps, Daniel Chartier |
5/11/2011 6:15 PM | |
Posts: 947 Rating: (45) |
Small text in addition: First You migrate project to Wincc 6.0, second migrate result to 7.0 |