Very interesting project to use 2 basic PLCs to achieve redundancy but without synchronization. However, if you want or need synchronization, that same Siemens doc sect 11.8 shows it can be achieved with lots of cross PLC A dig-out -> PLC B dig-in, and PLC B dig-out -> PLC A dig-in. Then outputs could be relatively closely synchronized. Do you have a 3rd PLC monitoring the 2 redundant PLCs for proper operation? Just curious how far you have gone down the path.
|
||||||
science guy |
|||||||
4/22/2021 4:03 AM | |
Joined: 9/2/2014 Last visit: 3/18/2024 Posts: 10 Rating: (1) |
Very interesting project to use 2 basic PLCs to achieve redundancy but without synchronization. However, if you want or need synchronization, that same Siemens doc sect 11.8 shows it can be achieved with lots of cross PLC A dig-out -> PLC B dig-in, and PLC B dig-out -> PLC A dig-in. Then outputs could be relatively closely synchronized. Do you have a 3rd PLC monitoring the 2 redundant PLCs for proper operation? Just curious how far you have gone down the path. ========== Thanks Einstien, I plan to use Synchronization between two CPUs by using : 1. One of the Q0.x designated as heartbeat in each CPU which fed to both CPUS as input I0.0 and I0.1 to derive alogic state on the health of each CPU. 2.The two CPU are interconnected via ethernet cable through PN port for exchange , a synchronization DB for exchange and verification of I/O image and Setting parameters and current data at the end of each scan. 3. Further logic under development. But I do not see any problem to achieve a parallel redundancy in case of two healthy CPUs or Takeover in Mono mode in case one CPU drops out. Third PLC may not be necessary. (Also the space of 530mm x 330 mm of mounting plate is limited in Ex-d enclosure considering I have to house a incoming Surge arrester , 3 off 2-pole AC incoming , 2 x 24 VDC Power Supply , A redundancy Coupler , Cartridge fuses, A Ethernet hub , 6 relays). Thanks for your interest. Kamath |
4/22/2021 4:15 PM | |
Joined: 7/7/2010 Last visit: 11/6/2024 Posts: 15385 Rating: (2443)
|
For the 24VDC supplies, might I suggest P/S intended to be operated IN PARALLEL so you only have one power source, but 2 supplies feeding power. This reduces terminals, reducing panel footprint. I have used parallel SOLA supplies, but Siemens offers 24VDC supplies as well as 24VDC UPS which can operate well together to provide power for a variety of project needs. No, I don't work for SIemens, nor SOLA. I just want to suggest an option that should reduce risk while not costing a lot. |
science guy |
|