Hi everyone, I am using pcs7 V9.1 SP1. I added the APLCustomerUnits.XML to the folders, however when I go see the unit (unit id = "2"). I see the undefined message? Could someone assist with this? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/30/2022 14:21:18New subject after splitting |
|
7/4/2022 8:07 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Lood09, Have you copy the xml-File to all OS-Servers and OS-Clients? It is necessary that all OS-Clients and OS-Server has the xml-File (see the manual PCS 7 Advanced Process Library at sectionSelecting a unit of measure). The XML is read-only once when WinCC runtime is activated. If any changes are done in the XML later, you must deactivate, close, and activate the WinCC runtime again to reflect the changes. And if the two options not help can you send the your adapted xml-file. Maybe there is something wrong. With regards |