Dear customer, regarding your questions: The EM23x has only a 0..20mA mode. You should adjust the process variable and the span. RNorm=((Rraw/Span)+Offset) Example: (14080-6400) ------------------- + 0.0 = 0.3 (32000-6400) The offset 0.5 is only for bipolar values. You should use the PID assistant in Step7-Microwin. The assistants up to Microwin V.3+SP4 don't contain a normalisation for the setpoint. This must be done by the user. Form Microwin V3.2+SP4 (V3.2.4.27) the PID assistant contains the normalisation for setpoint too. Please place S7-200 related topics in the section "Simatic S7-200". Your Technical Support |