4/24/2018 12:07 PM | |
Joined: 5/4/2015 Last visit: 5/9/2024 Posts: 19 Rating:
|
hi, I have a problem with the control cards (6SE7090 0XX84 0AF0) taken out from 2.2 KW and 45 KW drives. I was trying to install the 2.2 KW drive's control card on the 45 KW drive's control card as both of them having the same seimens code. I did this because of two reasons, one - as these are obsolete and second, to have a spare card for 45 KW drive. 1. All the parameter got download but few not copied because of the version mismatch (2.2 KW - 3.3 Version and 45 KW is 3.4 Version). How to solve the version difference problem and does this version deference really matter? 2. When I tried to manually put all parameters I was not able to change the KW from 2.2 to 45 (P070, P072, P073). How to solve this problem? For further understanding please find the attached zip file and the images in it. regards rahul AttachmentSimovert.zip (142 Downloads) |
4/25/2018 10:09 AM | |
Joined: 10/11/2006 Last visit: 8/27/2024 Posts: 5901 Rating:
|
Hello, first, you should upgrade to the same firmware version, for example this one or you search for other version. Then you need to do a power section definition according to chapter 6.3.1 of the manual. |
With best regards, |
|
Follow us on