5/28/2021 7:12 AM | |
Posts: 39 Rating: (9) |
Hi, You will not find MSTP device on Bacnet discovery. I guess you have to configure RS-485 port first for MSTP device. |
5/28/2021 9:06 AM | |
Joined: 5/28/2021 Last visit: 8/1/2024 Posts: 10 Rating: (3) |
I already configured COM1 in PXC5 as MSTP port. |
5/28/2021 2:40 PM | |
Joined: 6/4/2010 Last visit: 9/30/2024 Posts: 387 Rating: (130)
|
Dear forum member, I generally recommended to assign PXC4 MS/TP controller in the ABTsite offline engineering. However, if the devices have to be assigned online, first locate the network number of the MSTP port on the PXC5. Then configure the correct network number and the Discovery Scope «remote network» in the WEB interface of the PXC5. After the discover the available devices appear in the web interface. Please see the attached document for further information. Best regards, Albis AttachmentPXC4_M16MSTP_IntegrationToPXC5_E003.docx (542 Downloads) |
This contribution was helpful to2 thankful Users |
5/29/2021 7:04 AM | |
Joined: 5/28/2021 Last visit: 8/1/2024 Posts: 10 Rating: (3) |
Dear Albis, Thanks. It worked after I changed the network number to other number instead of 1. Regards, |