Joined: 4/2/2020 Last visit: 8/7/2022 Posts: 2 Rating: (0) |
Here's the screenshot. Thanks. |
7/18/2022 10:27 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello please have a look into capture 9 diagnostics SIMOTION D4x5-2, Commissioning and Hardware Installation Manual https://support.industry.siemens.com/cs/ww/en/view/109801510 If SIMOTION RT is ok --> Status 7LED-display after cyxle the power starts up and ends with "6 " as your picture shows and flashing "point" . If the point is not flashing the RT is not running --> link Status LED: https://support.industry.siemens.com/cs/ww/en/view/109781516 |
With best regards, |
|