Dear LGoossens_Integ, i don't think its possible via webserver. But maybe you can work with the instruction "T_CONFIG". If there are HMI's in the different modules, you can trigger this with the panel. Description T_CONFIGMaybe this helps regards sancruz |
Feedback appreciated, please rate |
|
This contribution was helpful to1 thankful Users |
5/3/2021 9:33 AM | |
Joined: 3/30/2020 Last visit: 10/4/2024 Posts: 4821 Rating: (987) |
Hello sancruz. You have the right idea. I had some issue when I tried to use it. I resolved my problem when I also assigned the Profinet name. Perhaps LGoossens_Integ can have a look at the attached SCL code and confirm if it works for their project. ~ AttachmentWriteIP.zip (851 Downloads) |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to2 thankful Users |
6/2/2021 6:13 PM | |
Joined: 7/7/2010 Last visit: 10/4/2024 Posts: 15264 Rating: (2422)
|
The Simatic Automation Tool ( https://support.industry.siemens.com/cs/document/98161300 ) would do what you are asking about. Does not require TIA Portal. Gives you ~28 days for the trial license.
|
Last edited by: 0_Einstein at: 06/03/2021 02:43:20Ooops, correction, for s7-1500 science guy |
|
5/9/2022 1:53 PM | |
Joined: 7/11/2019 Last visit: 8/28/2024 Posts: 31 Rating: (0) |
Hello, here is my change Ip project (tia 17) trough web (through watch table). Credentials: admin / admin. Hope it will be helpful.
AttachmentProjectChangeIpWeb.zip (596 Downloads) |
5/9/2022 1:54 PM | |
Joined: 7/11/2019 Last visit: 8/28/2024 Posts: 31 Rating: (0) |
Screenshot from my previous post: |
5/9/2022 4:36 PM | |
Joined: 3/30/2020 Last visit: 10/4/2024 Posts: 4821 Rating: (987) |
Hello. The example you provide is very heavy. Using 45% of work memory and 9% load memory on a CPU1211. The consumption of the design is because of using a Siemens provided library: I find it strange that you have elected to remove the comment block in the code that states that the LPNDR library was developed originally by Siemens. I would encourage you to keep the original library code with comment as is. Or if stuff is added, to add comments in the change code history. Have you tested your design?.. Does the IP address change while the PLC is still in RUN mode? ~ |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|