Dear Ganes, Is there any extention modules of digital IO's in s71200 series on ethernet
|
1/4/2013 7:56 AM | |
Joined: 8/31/2010 Last visit: 7/18/2025 Posts: 1525 Rating:
|
Hello m.shoaib khatana, You can not use the signal modules of S7-1200 directly on Remote IO. Whereas ET200SP must be a ideal solution if you look for a Distributed IO on Etherenet. For more info - www.siemens.com/et200sp |
Like it? Rate it! |
|
This contribution was helpful to
1 thankful Users |
2/11/2013 3:42 PM | |
Joined: 8/31/2010 Last visit: 7/18/2025 Posts: 1525 Rating:
|
Hello m.shoaib khatana, You can communicate 10 nos. S7-1200 to a central S7-1200 CPU, but keep in mind that it's not possible - all at the moment (all 10 CPU communicating to 1 central CPU). As you can find the limitations of the number of connections from here - With which devices can the S7-1200 communicate over the integrated PROFINET interface and which protocols does the S7-1200 support? Regarding WinCC v7 with S7-1200 - You cannot communicate S7-1200 directly with WinCC v7 - whereas there is a workaround for it. Communicate the S7-1200 data via OPC in WinCC v7 How do you configure an S7 connection for the OPC server of a PC station in STEP 7 Professional V11 (TIA Portal) to access the data of an S7-1200 over Industrial Ethernet? |