Check page 27 in the document 109744660, It explains NAT Variants with the Scalance S615. I had a similar problem where I did not want to change the Gateway settings on my PLC's at the site, I had a S612 and it was not possible to get there unless I set the PLC default gateway as Siemens S612 private side address. I could not get there with the S612, so I upgraded to a S615. I followed the example on p.27 and it worked no problem. I am now able to Connect from Public side to private side to the PLC and the PLC does not require a Gateway set for it. It looks like you can do a connection using "double NAT" https://support.industry.siemens.com/cs/ww/en/view/109744660 Dave |