2/19/2010 8:21 AM | |
Posts: 2930 Rating: (432)
|
Hi, here an example for both sensors. Range is 0..25Bar and -1..20Bar. If you delete each second Analog Amplifier in the line, then the range is 0..250 and -10..200. Hope this helps AttachmentScalling 4..20mA.zip (583 Downloads) |
2/19/2010 10:13 AM | |
Posts: 661 Rating: (123) |
If you cannotrepresentthe value range because of internal calculation, -> minimize the calculation error. If 0-25 Bar can only be defined as 0-24 Bar (1Bar difference), use a better resolution. -1 to 2503 would be suitable here. So you have shifted the calculation error tothe second decimal place and it doesn´t matter any more. AttachmentScaling 4..20mA_2.zip (580 Downloads) |
2/19/2010 6:17 PM | |
Posts: 7 Rating: (0) |
thanks now I understand how to do it :) |